Buderus GB172i.2 (BC400) flowtemp support #1755

Answered by MichaelDvP
molszowy asked this question in Q&A
Discussion options

You must be logged in to vote

@molszowy
Yes, without thermostat you can set the flowtemp with emsesp, many users do this.

  • the flowtemp on the controlpanel have to be set higher, the temperature send over the bus is only accepted if lower.
  • you have to send at least every minute, otherwise the boiler fall back ti the higher setpoint from the control.
  • we have a special entity forceheatingoff that sends every minute a flowtemp 0 to the boiler, some users like to use a on/off control.