Many thanks for the great integration I have two SE inverters - SE5000H and SE5000 plus a StorEdge with an LG battery connected to the 5000. I want to be able to charge from grid. I can change the setting in HA for the SE5000 but keeps on immediately resetting itself to Maximise Self Consumption. Have tried changing which unit is Master /Slave, disconnecting from monitoring, plus pretty much every other setting I can think of but still stubbornly does same thing. Everything else working ok and can see on panel the battery starting to charge so seems to be something at the inverter. Any ideas as to how I can fix ? Many thanks in advance for any ideas / suggestions. |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment
-
For others who might have same issue, the problem here was my master inverter which had the wifi was also the master. The meter and battery were on the second inverter which was a slave. I fixed by making the inverter with the meter the master and a hard wired meter connection. Could see occasional Comms issues between master and slave in original configuration eg when in SetApp. Think this was causing the self consumption to glitch when the old master couldn’t communicate with the meter. Working perfectly now. Happy days ! |
Beta Was this translation helpful? Give feedback.
For others who might have same issue, the problem here was my master inverter which had the wifi was also the master. The meter and battery were on the second inverter which was a slave. I fixed by making the inverter with the meter the master and a hard wired meter connection. Could see occasional Comms issues between master and slave in original configuration eg when in SetApp. Think this was causing the self consumption to glitch when the old master couldn’t communicate with the meter. Working perfectly now. Happy days !