Replies: 3 comments 5 replies
-
Same for me. "Outdoor air temp" gets stuck as soon as I turn off the HP. |
Beta Was this translation helpful? Give feedback.
-
I suspect this will be from having the power saving function enabled. I have the same on my EDLA04 unit and the functionality is described on page 58 of this doc: https://www.daikin-ce.com/content/dam/document-library/Installer-reference-guide/heat/air-to-water-heat-pump-low-temperature/EBLA04-08EV3.EBLA04-08E3V3.EDLA04-08EV3.EDLA04-08E3V3_Installer%20reference%20guide_4PEN685228-1B_English.pdf "When the power saving functionality of the outdoor unit is active (see "Power saving function" [4212]), the outdoor unit is turned down to reduce standby energy losses. As a result, the outdoor ambient temperature is NOT read out." Something I have noticed is the external outside temperature sensor is reporting its values in "Ext. indoor ambient sensor (R6T)" and this is updated even when the pump is in standby mode. |
Beta Was this translation helpful? Give feedback.
-
Hello,
I have indoor unit EHVH08S23EJ6V and outdoor unit ERGA06EAV3H and have an issue with "Outdoor air temp.(R1T)"
I am using definition "ALTHERMA(LT_CA_CB_04-08KW).h"
{0x20,0,105,2,1,"Outdoor air temp.(R1T)"}, is not updating and stays constantly on the same value.
Does anyone have an idea to solve the issue or am i using the wrong definition?
All other configured values are woking and also being updated.
Beta Was this translation helpful? Give feedback.