Replies: 5 comments
-
There was a whole thread about this in #466 85 is indeed an invalid reading, typically from cheaper DS18B20 clones. I thought in EMS-ESP we filter them out and don't send the MQTT payload but I couldn't find it in the code (@MichaelDvP do you remember?) |
Beta Was this translation helpful? Give feedback.
-
@proddy You have already referenced #466. As harvey637 wrote, 85°C is a sign of underpower. But it is in the valid range, so we dont filter it. The guy in #466 have used parasite sensors, but i think not enabled parasite powering. (instead lower pullups). I guess this case is similar, the sensor reports one/some 85 values and then gives error. After 5 errors in row the sensor is removed. But without any information about the system it's only a guess. |
Beta Was this translation helpful? Give feedback.
-
thanks @MichaelDvP . Your brain is like an elephant. Can you take this one? |
Beta Was this translation helpful? Give feedback.
-
Ok, as far as i see we only need a
to remove the broken sensor from HA. (as for device values). |
Beta Was this translation helpful? Give feedback.
-
in dev-16 |
Beta Was this translation helpful? Give feedback.
-
I'm using EMS-ESP v3.4.4 with MQTT auto-discovery in Home Assistant. When a Dallas sensor reports 85,0 °C, the value is not available in the MQTT payload, and Home Assistant reports a warning:
Ideally the
temp
attribute should be set to the value of the Dallas sensor (85,0 °C
), or it could even be set tonull
to report to Home Assistant that no valid temperature is available.Beta Was this translation helpful? Give feedback.