Hi
I am trying to perform load flow and fault study in Pandapower. I have results from opendss studies for the same circuit. I have a bus "zero" connected to an external grid of known short circuit capacity (s_sc_max_mva=352 MVA).
After running the load flow, the result for this bus (slack bus) is v=1.00 pu. However, as I understand the situation, the system is not considering the voltage drop in the source impedance (about 5% in my case).
Running the same study in Opendss (EPRI), I get the correct result for bus "zero" which is then called "sourcebus".
In order to have comparable results I have to manually insert one impedance element after between bus "zero" and the main substation bus (bus "b1"). I found no reference in the documentation on how to tackle this issue.
Now, in the fault study, it seems that Pandapower accounts for the source/external grid impedance because the results are similar to those from Opendss.
Would someone help me ?
reacted with thumbs up emoji reacted with thumbs down emoji reacted with laugh emoji reacted with hooray emoji reacted with confused emoji reacted with heart emoji reacted with rocket emoji reacted with eyes emoji
-
Hi
I am trying to perform load flow and fault study in Pandapower. I have results from opendss studies for the same circuit. I have a bus "zero" connected to an external grid of known short circuit capacity (s_sc_max_mva=352 MVA).
After running the load flow, the result for this bus (slack bus) is v=1.00 pu. However, as I understand the situation, the system is not considering the voltage drop in the source impedance (about 5% in my case).
Running the same study in Opendss (EPRI), I get the correct result for bus "zero" which is then called "sourcebus".
In order to have comparable results I have to manually insert one impedance element after between bus "zero" and the main substation bus (bus "b1"). I found no reference in the documentation on how to tackle this issue.
Now, in the fault study, it seems that Pandapower accounts for the source/external grid impedance because the results are similar to those from Opendss.
Would someone help me ?